110V or 220V how to tell

Here's a Pic of a hotub run at a new house we bought.

The spa itself is 110V but I always thought 50A breakers were 220V.

50A Breaker
20A left marked Garage
20A right marked Spa

Anyway - how do I tell ....... whats what

__________________
FAKKY 57 PANEL BUILD
FAKKY is offline   Reply With Quote
Old 08-08-2018, 04:31 PM   #2
Coley
Registered User
 
Coley's Avatar
 
Join Date: Oct 2011
Location: Victoria, B.C
Posts: 3,794
Re: 110V or 220V how to tell

Is the jacuzzi....a jacuzzi tub?...vs. a 'Hot Tub' (much bigger)...which would make sense on a 110V system.
Most hot tubs run a 220V because they need that power to not only run the big pumps but also to produce the heat.
Looks like someone wired that in themselves maybe...which is perhaps why there is a 50 amp breaker in there...it looks to be a GFCI, so why is the jacuzzi listed on a small non-GFI breaker?

Is that black wire on the right the only 'feed' into the box? (12/2?...it almost looks like it doesn't have a ground, lol)
How far does the black wire run until it joins into its main feed?...and where does it originate from? (the main panel? or a junction box? or is it tapped off an outer house plug inside or outside?)
If it does connect into a larger (main?) panel of junction box is there a breaker on it to isolate this system and shut if off?

(note: the best way to tell what is going on inside there in terms of wiring is to remove that front plate...but unless you know what you are doing and confident around electricity its best to disable the panel first from the feeder panel that supplies it...noting that I don't think there is such a thing as a 50 amp breaker for a 110 volt system- nope)

Lets start with a bit more information so we can figure this out.

Coley
__________________
....for some men, there is experience, skill and effort....for the others...there is visa and UPS LOL
1966 Chevy 1/2 ton (Florida- Red/white)
1972 Chevy 1/2 ton (California- Blue/white)
2005 Chevy Silverado HD2500/Duramax
2000 Dodge Ram 1500

Last edited by Coley; 08-08-2018 at 04:42 PM.
Coley is offline   Reply With Quote
Old 08-08-2018, 04:45 PM   #3
Coley
Registered User
 
Coley's Avatar
 
Join Date: Oct 2011
Location: Victoria, B.C
Posts: 3,794
Re: 110V or 220V how to tell

Something of note here:
It isn't uncommon for people to wire these things up themselves through variety of methods but most of all...through a variety of wire types and styles.
The wire needed to run a 220 volt hot tub (which is what 95% are) that is 40-50ft from the main panel is a pretty serious wire...usually a 6/3....and if you get off lucky it is an 8/3.
Now, whats the big deal?....price 60-75ft of either of these out at Home Depot or your local supplier. ....you will be surprised at how expensive they are...hence the improvisation by some home owners to try to work around this.
That said...the right wire....a big 6/3 is the way to go. (thats what I used....painfully paid for....but still used, lol)
You want to be safe....from fire and from electrocution....not the place to monkey around for sure.

All good
Coley
__________________
....for some men, there is experience, skill and effort....for the others...there is visa and UPS LOL
1966 Chevy 1/2 ton (Florida- Red/white)
1972 Chevy 1/2 ton (California- Blue/white)
2005 Chevy Silverado HD2500/Duramax
2000 Dodge Ram 1500
Coley is offline   Reply With Quote
Old 08-08-2018, 05:58 PM   #4
Indian113
Registered User
 
Indian113's Avatar
 
Join Date: Sep 2009
Location: Monroe,Iowa
Posts: 4,370
Re: 110V or 220V how to tell

I had a 110 volt Hot Tub, But it was only a 4 person tub. Electricity and Water = Death! I would hire someone that Knows what they are doing to fix it.
Indian113 is offline   Reply With Quote
Old 08-08-2018, 06:09 PM   #5
jeffahart
Senior Member
 
jeffahart's Avatar
 
Join Date: May 2012
Location: Scottsdale, AZ
Posts: 1,882
Re: 110V or 220V how to tell

Two pole. Take off the dead front cover and look at it. My biggest concern would be if it is 50A and not over fused; and if the grounded neutral and grounding buses are setup correctly. I would get a different panel and add more breakers for more stuff too.


J
__________________
White K20
jeffahart is offline   Reply With Quote
Old 08-08-2018, 06:49 PM   #6
100%Chevy
Registered User
 
Join Date: Jun 2008
Location: Moss Point,Ms.
Posts: 1,439
Re: 110V or 220V how to tell

I'm a retired licensed,bonded and master electrician.
The very best advice I can give is to call out the same type electrician to look at and verify that it is wired correctly!
When your life is involved,don't take chances or free advice(even well meaning)do it right!
For what it's worth---more people are electrocuted at home than anywhere else!
Mike.
100%Chevy is offline   Reply With Quote
Old 08-08-2018, 10:51 PM   #7
pritch
Registered User
 
pritch's Avatar
 
Join Date: Mar 2004
Location: Hoytsville, Utah
Posts: 3,365
Re: 110V or 220V how to tell

Quote:
Originally Posted by 100%Chevy View Post
I'm a retired licensed,bonded and master electrician.
The very best advice I can give is to call out the same type electrician to look at and verify that it is wired correctly!
When your life is involved,don't take chances or free advice(even well meaning)do it right!
For what it's worth---more people are electrocuted at home than anywhere else!
Mike.
What he said.
__________________
'68 Panel
Project Boogie Chillin'
'68 C-10
Ol' Green
pritch is offline   Reply With Quote
Old 08-09-2018, 12:09 AM   #8
Steeveedee
Who Changed This?
 
Steeveedee's Avatar
 
Join Date: Jan 2013
Location: Simi Valley, CA
Posts: 10,088
Re: 110V or 220V how to tell

Quote:
Originally Posted by pritch View Post
What he said.
X2. You need to make certain that what is behind that panel is properly done. I have a friend who spent 9 months in a burn ward after building a natural gas heated sauna, with just one flaw.
__________________
~Steven

'70 Chevy 3/4T Longhorn CST 402/400/3.56 Custom Camper

Simi Valley, CA
Steeveedee is offline   Reply With Quote
Old 08-09-2018, 09:48 AM   #9
rpmerf
Registered User
 
rpmerf's Avatar
 
Join Date: Feb 2011
Location: Parkville, MD
Posts: 1,024
Re: 110V or 220V how to tell

110 will have 1 hot
220 will have 2 hots
Look for a model number on the tub and google for a manual.
__________________
1970 C20 Custom Camper - 350, TH350
1997 GMC Suburban
1994 Acura Integra GSR
1987 Dodge Daytona Shelby Z
rpmerf is offline   Reply With Quote
Old 08-09-2018, 09:57 AM   #10
FAKKY
Registered User
 
Join Date: Sep 2016
Location: Redington Beach
Posts: 1,312
Re: 110V or 220V how to tell

Sorry guys been tied up.

1) Im not touching the electric [fixing anything] - just trying to work out whats what.
2) I know nothing.

It appears the main black thick wire is coming from teh main junction box inside the house. Its NOT marked ...... but Im *guessing* its the 50A at positions 28+30







I generally wont touch anything over 12V except for putting in light/fan fixtures etc.
But I would liek to understand more so when I converse with contractors I dont feel like an idiot. So a bit of

A) My current configuration
B) General how to .... links ... whatever.

Another Example is I have that 50A subpanel under the spa. An I have a 100A panel in the garage. No idea if the 100A is linked to the main panel or a seperate run .....but I dont see anything listed in the main house panel.

So on.
__________________
FAKKY 57 PANEL BUILD

Last edited by FAKKY; 08-09-2018 at 10:02 AM.
FAKKY is offline   Reply With Quote
Old 08-09-2018, 11:52 AM   #11
Boog
laying low
 
Boog's Avatar
 
Join Date: Mar 2001
Location: Searcy, Ark. USA
Posts: 12,957
Re: 110V or 220V how to tell

Difference between 110 and 220?
110 will buzz you and you can get loose. 220 can get you and you might not get loose from it. So i’m told. I’ve been buzzed a couple times.
Be careful.
__________________
Boog
69 Chevy stepside, 358/T350, 4.11 posi, 4.5/4 drop, rallys, poboy driver
primer is finer
91 Chevy sportside, Tahoe, Yukon & GMC Crewcab All GM..'nuff said.

I stand for the flag and kneel at the cross
Boog is offline   Reply With Quote
Old 08-09-2018, 12:05 PM   #12
jeffahart
Senior Member
 
jeffahart's Avatar
 
Join Date: May 2012
Location: Scottsdale, AZ
Posts: 1,882
Re: 110V or 220V how to tell

It was probably installed and wired correctly, assume that. Why not just leave it alone? If you are concerned get a contractor to inspect it. If you are adding appliances and need more current or circuits... get a contractor. I install my own panels, but that's me, I pull permits. You can goto building and safety and see any permits. But if you are concerned, I'm sure a simple inspection will put your mind at ease

Like said above, most snake bites are on the hands of people trying to pick up a snake. Same applies to electricity.

Enjoy your home and be safe!


j
__________________
White K20
jeffahart is offline   Reply With Quote
Old 08-09-2018, 12:08 PM   #13
Ol Blue K20
Proprietor of Dale's Corner
 
Ol Blue K20's Avatar
 
Join Date: Nov 2012
Location: Vacaville , CA
Posts: 15,834
Re: 110V or 220V how to tell

You need to have an electrician trace out how things are run. Without tracing it out we're just guessing. Be safe.
__________________
"Some Days Chickens And Some Days Feathers"

Dale
XNGH ECV Sam Brannan 1004

R.I.P. 67ChevyRedneck
R.I.P. Grumpy Old Man
Ol Blue K20 is offline   Reply With Quote
Old 08-09-2018, 01:03 PM   #14
FAKKY
Registered User
 
Join Date: Sep 2016
Location: Redington Beach
Posts: 1,312
Re: 110V or 220V how to tell

Quote:
Originally Posted by jeffahart View Post
It was probably installed and wired correctly, assume that. Why not just leave it alone?

j

AS mentioned ----- not trying to change or alter anything.
It started with a simple question from SPA company asking me if I had 110V or 220V existing RUN.

I said - no idea. Felt a bit dumb. Just wanted to learn a bit more.

Assume its something like .....

1) Disconnect the main breaker at the main panel box
2) Remove exterior panel to see fuse/circuit behind panelling at SPA 50A sub box.
3) use a basic electric detector to ensure no electricity (not hot)
4) Look for TWO BLACK wires plumbed in ...... together with a single white and single copper ?

Something to that affect ?


Just re-iterating ....... not doing anything if its HOT .... and even if not hot ..... still only validating .... not going to be responsible for wiring anything over 12V auto .

Just want to be more "versed", better understanding of whats going on in my home etc.
__________________
FAKKY 57 PANEL BUILD
FAKKY is offline   Reply With Quote
Old 08-09-2018, 01:12 PM   #15
jeffahart
Senior Member
 
jeffahart's Avatar
 
Join Date: May 2012
Location: Scottsdale, AZ
Posts: 1,882
Re: 110V or 220V how to tell

They should be on site to do the estimate. Then they can tell you what you have and what you need as far a electrical or gas upgrades. They will/should include it in their estimate. They should tell you if you need permits and pull any necessary permits.

Don't feel dumb. You can't possibly know everything. Ask the contractors when they are on site. You will learn more and more about your home overtime.


j
__________________
White K20
jeffahart is offline   Reply With Quote
Old 08-09-2018, 02:11 PM   #16
100%Chevy
Registered User
 
Join Date: Jun 2008
Location: Moss Point,Ms.
Posts: 1,439
Re: 110V or 220V how to tell

Actually,you're one of the smarter ones!
You've asked first!
I only posted because,I don't want to see anyone hurt when they seem a little unsure of themselves.
If you want to know for sure what's what and what is required,you can call your local code enforcement office(inspections dept.)
They will usually come out and check your new home for you for a small inspection fee.Less than an electrician would charge.
Be aware,they will also probably make you repair any problems they find.
A great reference book for anyone is "Ugly's Electrical References".
should be able to find it on-line,although I haven't tried myself,because I have it.
Mike.
100%Chevy is offline   Reply With Quote
Old 08-09-2018, 04:06 PM   #17
truckster
Senior Member
 
truckster's Avatar
 
Join Date: Jan 2001
Location: Orem, Utah
Posts: 7,796
Re: 110V or 220V how to tell

IF the box is correctly labeled, it's 110v. The breaker labeled "Jacuzzi" is a single pole breaker, and it would only be carrying 110v.
__________________
I have sworn upon the altar of God, eternal hostility against every form of tyranny over the mind of man. - Thomas Jefferson
truckster is offline   Reply With Quote
Old 08-09-2018, 04:10 PM   #18
cypressbog
Go Pack Go!
 
Join Date: Nov 2005
Location: Green Bay
Posts: 2,669
Re: 110V or 220V how to tell

Aren't the plugs different? 110 is your normal looking household plug. The 220 plug is larger and has various different terminals.
cypressbog is offline   Reply With Quote
Old 08-09-2018, 05:04 PM   #19
100%Chevy
Registered User
 
Join Date: Jun 2008
Location: Moss Point,Ms.
Posts: 1,439
Re: 110V or 220V how to tell

Quote:
Originally Posted by cypressbog View Post
Aren't the plugs different? 110 is your normal looking household plug. The 220 plug is larger and has various different terminals.
There are over 200 NEMA specific receptacles and plug ends on the charts!
Each has it's own voltage and amperage rating.Unless it's where you can read the numbers on it,it's really hard to guess what it is.
Just from the pic,I believe it"s a 120 volt,single phase box.the GFCI breaker appears to be a double, but more than likely it's just using 2 tabs off the same 120 volt bus to get more amperage than a single tab can provide.But,I'm just guessing!
Mike.
100%Chevy is offline   Reply With Quote
Old 08-09-2018, 08:43 PM   #20
FAKKY
Registered User
 
Join Date: Sep 2016
Location: Redington Beach
Posts: 1,312
Re: 110V or 220V how to tell





Thanks guys.
__________________
FAKKY 57 PANEL BUILD
FAKKY is offline   Reply With Quote
Old 08-09-2018, 10:55 PM   #21
pritch
Registered User
 
pritch's Avatar
 
Join Date: Mar 2004
Location: Hoytsville, Utah
Posts: 3,365
Re: 110V or 220V how to tell

You know, that 50 you're pointing at in the picture-it's not installed correctly and, help me with this sparkies, I'm not even sure it's correct for that panel, and that could be why it's not snapped in. All the others are clearly marked Square D, that one is not.
__________________
'68 Panel
Project Boogie Chillin'
'68 C-10
Ol' Green
pritch is offline   Reply With Quote
Old 08-10-2018, 12:53 AM   #22
Coley
Registered User
 
Coley's Avatar
 
Join Date: Oct 2011
Location: Victoria, B.C
Posts: 3,794
Smile Re: 110V or 220V how to tell

Some good advice and insight here.....some opinions lighter, some heavier...but all good.
It looks like its worth taking a little closer look at.
Maybe see if you can find a buddy (or an electrician) to take a quick peak at this and see if its going to work for you and be safe.

All Good
Coley
__________________
....for some men, there is experience, skill and effort....for the others...there is visa and UPS LOL
1966 Chevy 1/2 ton (Florida- Red/white)
1972 Chevy 1/2 ton (California- Blue/white)
2005 Chevy Silverado HD2500/Duramax
2000 Dodge Ram 1500
Coley is offline   Reply With Quote
Old 08-10-2018, 01:13 AM   #23
'63GENIII
Registered User
 
'63GENIII's Avatar
 
Join Date: Sep 2008
Location: San Carlos, Ca.
Posts: 3,048
Re: 110V or 220V how to tell

Fakky, one important thing to remember is it only takes 5 milliamps to interrupt the signal that makes the heart work. Period. Regardless of the voltage.

Ive been bit by 480v that scared the bejezuz outta me yet stayed at work, and then been "hung up" by the 48 - 90 volts DC that runs on our phone lines and been sent to the hospital. Its all about the 1000s of variables that come together when you get lit up that determine whether you get a second chance to respect it.

The cable that is run into your Jacuzzi sub panel is an 8-3 or 6-3 Romex. Might even be a 4-3. In any case it is a 3 wire. If connected by an electrician, should be 120/240 volt present. There should be 2 hot phases, a neutral and a ground in that wire. And yes, its still called a 3 wire even though there are 4 conductors in it.

I would get an inductance or "tick tracer" (a good Fluke is reasonable $$ and as accurate as you can get) and check to see which breaker feeds that sub panel. Yes, could be a few trips back and forth between the main panel and that sub panel feeder (the 3 wire cable)and you should be able to tell when the sub panel is dead. A good tick tracer will read through the jacket on that cable. Spend the money (20$) and get the fluke.

Once you can determine which breaker de energizes that sub panel, you can shut it off, CAREFULLY open the sub panel and check with a real voltage tester - Wiggy or Knopp to be absolutely sure there is no voltage present. This cannot be stressed enough. No voltage present at any of the wire terminations to ground or to neutral. If you cannot check this correctly or feel uncomfortable doing it, call an electrician.

For that main panel, same rules apply. Open the main (the 4 pole breaker on the top). I would strongly consider getting a qualified AND trusted electrician to do this. There's not a lot of room for learning here and the learning curve is like a wall when it comes to not making mistakes.

One thing I will say is that it looks as though you have Square D Homeline breakers in an ITE / Siemens or Cutler Hammer Panel. Different manufacturers. Likely why that 2 pole 50 doesn't fit and would certainly void any kind of liability from either manufacturer and quite possibly your insurance should something happen. Each manufacturer has its own breakers that their panels are UL tested with. Most of the time they just don't interchange or fit well. Sometimes they won't do their job right when mixed. That is where the problems start. If you do have a City Inspector look at your panel and he doesn't call it out, he doesn't know his head from a hole in the ground and should be sent packing...with all due respect of course.

An easy way to safely identify what is controlled by which breaker is to set aside a little bit of time, turn off one breaker at a time and see what turns off / on. It is way cheaper for you to do this than it is for you to pay someone to do it for you. This will give you a little better knowledge / insight into what you have which will also make it easier to communicate to the electrician what your desired end result should be.

One other good tester is made by Gardner Bender and is a "plug in" tester. They are great for testing u ground (the type in your house) receptacles. Most will let you know if the plug polarity is right, ground and neutral isn't reversed and most these days will test the operation of a GFCI plug.

Feel free to PM me with any ???s you may have. Been an electrician for 30 years this year. Wired everything from turbine generators to swimming pools to playhouses and have seen and repaired some of the strangest homeowner installs in that time.

Be safe.
__________________
Chris


'63 k15 long step
Vortec 7.4 - L29 Blackbear tune, Five 0 Motorsports injectors, Chris Straub Cam, NV4500, divorced 205
52" front and 63" rear spring swap
D44 / 14bff - disc axles
Milemarker 9K and 10.5K hydraulic winches

63" & B52 Spring Install http://67-72chevytrucks.com/vboard/s...ng+swap+thread


NV4500 Reverse Build Thread http://67-72chevytrucks.com/vboard/s...=reverse+build

L29 - 7.4 Vortec Build http://67-72chevytrucks.com/vboard/s...&highlight=L29
'63GENIII is offline   Reply With Quote
Old 08-10-2018, 07:39 AM   #24
FAKKY
Registered User
 
Join Date: Sep 2016
Location: Redington Beach
Posts: 1,312
Re: 110V or 220V how to tell

__________________
FAKKY 57 PANEL BUILD
FAKKY is offline   Reply With Quote
Old 08-10-2018, 02:56 PM   #25
'63GENIII
Registered User
 
'63GENIII's Avatar
 
Join Date: Sep 2008
Location: San Carlos, Ca.
Posts: 3,048
Re: 110V or 220V how to tell

Looks to be nothing connected to the GFI breaker? I would make sure there is a GFI in between the single pole 20 that is marked jacuzzi and the jacuzzi itself. There needs to be one to be protected.
__________________
Chris


'63 k15 long step
Vortec 7.4 - L29 Blackbear tune, Five 0 Motorsports injectors, Chris Straub Cam, NV4500, divorced 205
52" front and 63" rear spring swap
D44 / 14bff - disc axles
Milemarker 9K and 10.5K hydraulic winches

63" & B52 Spring Install http://67-72chevytrucks.com/vboard/s...ng+swap+thread


NV4500 Reverse Build Thread http://67-72chevytrucks.com/vboard/s...=reverse+build

L29 - 7.4 Vortec Build http://67-72chevytrucks.com/vboard/s...&highlight=L29
'63GENIII is offline   Reply With Quote
Reply

Bookmarks


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -4. The time now is 01:35 AM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2024, vBulletin Solutions Inc.
Copyright 1997-2022 67-72chevytrucks.com